2 minutes ago, eggsarascal said:

A 3 phase motor starts in star then switches over to Delta, you are pissing up the wrong tree, Les.

Your just being a prick now eggs. I am not telling the guy how to wire his setup  if it is an older type motor then that is what is needed, 

Edited by topchippyles
Link to comment
Share on other sites

Log in or register to remove this advert

5 minutes ago, eggsarascal said:

You want a row message me, let's leave it off these pages.

Is this close enough for you. You can argue over the most stupid things eggs. If i had not done it and paid out a vast some then i would not comment.

 

Rule of Thumb
Electric Motor Size Minimum Generator Req'd (KVA) by Starting Method
HP KW D.O.L to KVA Size (Note 1)
15 11 37.5
20 15 50
25 19.6 60.5
  • Like 1
Link to comment
Share on other sites

6 minutes ago, eggsarascal said:

A 3 phase motor starts in star then switches over to Delta,

Yes for big motors; when the motor starts from stationary each voltage cycle there is a sudden rush of current, and this creates a massive torque, once it is moving the squirrel cage armature starts generating a back electro motive force which opposes the supply voltage and reduces the current. With star delta it's effectively wired as a 240V motor as it comes up to speed as otherwise the inrush current on each cycle would likely overload the supply, once it's rotating sufficiently fast for the back emf to reduce the current even at the higher voltage it is switched to act as a 440V motor.

 

I agree that the rule of thumb is you need to supply 3 times the current to start up a motor because of this inrush. There are other ways around this by controlling the current  or the frequency

 

The Power=Volts x Amps is true but because a motor is an inductive load the current and voltage are out of phase so even when it is running at rated speed it will be drawing more amps  than the power suggests, which is why the motor will be rated at 15kW but the generator supplying it will need to supply the 15kW when the voltage is out of phase with the  voltage, so it will need more than 15kVA to run at rated power. Hence  the windings of the generator will need to be able to withstand the supply voltage and the higher current, which is why a generator is rated in kVoltsAmps rather then kWatt.

  • Like 3
  • Thanks 1
Link to comment
Share on other sites

14 minutes ago, openspaceman said:

Yes for big motors; when the motor starts from stationary each voltage cycle there is a sudden rush of current, and this creates a massive torque, once it is moving the squirrel cage armature starts generating a back electro motive force which opposes the supply voltage and reduces the current. With star delta it's effectively wired as a 240V motor as it comes up to speed as otherwise the inrush current on each cycle would likely overload the supply, once it's rotating sufficiently fast for the back emf to reduce the current even at the higher voltage it is switched to act as a 440V motor.

 

I agree that the rule of thumb is you need to supply 3 times the current to start up a motor because of this inrush. There are other ways around this by controlling the current  or the frequency

 

The Power=Volts x Amps is true but because a motor is an inductive load the current and voltage are out of phase so even when it is running at rated speed it will be drawing more amps  than the power suggests, which is why the motor will be rated at 15kW but the generator supplying it will need to supply the 15kW when the voltage is out of phase with the  voltage, so it will need more than 15kVA to run at rated power. Hence  the windings of the generator will need to be able to withstand the supply voltage and the higher current, which is why a generator is rated in kVoltsAmps rather then kWatt.

Spot on and the fact i put deta/star was just referring to the motor type not the way its wired up or starting current. Some people just have nothing better to do on a saturday afternoon. 

Link to comment
Share on other sites

What you could do is stick in an underrated power system and spend the savings on a fire extinguisher and a pair of trainers!

I love it when guys ask a question and argue when they don't get the answer they desire...no disrespect to the OP whom I hope is looking for a logical explanation and think he has it now!

 

  • Like 1
  • Haha 1
Link to comment
Share on other sites

24 minutes ago, spudulike said:

What you could do is stick in an underrated power system and spend the savings on a fire extinguisher and a pair of trainers!

I love it when guys ask a question and argue when they don't get the answer they desire...no disrespect to the OP whom I hope is looking for a logical explanation and think he has it now!

 

I put eggs in the same  (He be along now you watch) ?

 

 

download.jpg

Edited by topchippyles
Link to comment
Share on other sites

19 hours ago, openspaceman said:

Yes for big motors; when the motor starts from stationary each voltage cycle there is a sudden rush of current, and this creates a massive torque, once it is moving the squirrel cage armature starts generating a back electro motive force which opposes the supply voltage and reduces the current. With star delta it's effectively wired as a 240V motor as it comes up to speed as otherwise the inrush current on each cycle would likely overload the supply, once it's rotating sufficiently fast for the back emf to reduce the current even at the higher voltage it is switched to act as a 440V motor.

 

I agree that the rule of thumb is you need to supply 3 times the current to start up a motor because of this inrush. There are other ways around this by controlling the current  or the frequency

 

The Power=Volts x Amps is true but because a motor is an inductive load the current and voltage are out of phase so even when it is running at rated speed it will be drawing more amps  than the power suggests, which is why the motor will be rated at 15kW but the generator supplying it will need to supply the 15kW when the voltage is out of phase with the  voltage, so it will need more than 15kVA to run at rated power. Hence  the windings of the generator will need to be able to withstand the supply voltage and the higher current, which is why a generator is rated in kVoltsAmps rather then kWatt.

Soft starter, no need for a massive generator.

 

 

  • Haha 1
Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share


  •  

  • Featured Adverts

About

Arbtalk.co.uk is a hub for the arboriculture industry in the UK.  
If you're just starting out and you need business, equipment, tech or training support you're in the right place.  If you've done it, made it, got a van load of oily t-shirts and have decided to give something back by sharing your knowledge or wisdom,  then you're welcome too.
If you would like to contribute to making this industry more effective and safe then welcome.
Just like a living tree, it'll always be a work in progress.
Please have a look around, sign up, share and contribute the best you have.

See you inside.

The Arbtalk Team

Follow us

Articles

×
×
  • Create New...

Important Information

We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.