run a kemppi pss5000 welder with a genset?


Graham w
 Share

Recommended Posts

Log in or register to remove this advert

I'd go with no on that. You need 8kva to run my 180 amp Kemppi mig inverter to it's maximum according to the manual. A big old transformer beast like that with all the inrush current will probably destroy a generator windings in no time.

Link to comment
Share on other sites

I can see your point so had a look at the brochure and the 500 amp only requires a 28 kva and the 280 amp requires 7.2 kva power supply. i hope running the welder should be trouble free

 

found a company called Westermans that specialize in these old beasts, but they are not open on sundays:laugh1:

 

http://www.westermans.com/downloads/kemppi%20multisystem.pdf

 

by inrush current do you mean instant very high load?

Link to comment
Share on other sites

by inrush current do you mean instant very high load?

 

There's a big spike every time you arc up, probably I got the wrong name for it but if you weld on home electricity it can trip breakers but if you upgrade to a slower trip (from a B to a C) it will cope with the surge then continue as normal but generators don't cope with this so well. 7.2kva sounds a bit optimistic to run a 280 amp.

Edited by peatff
Link to comment
Share on other sites

im currently running the 350 amp rated at 13.2kva on the 20kva gen and seems to be happy enough. i think these welders are designed to have a low power consumption to make them more versatile. planning to run the 500 on a 100kva.

 

is there a way of protecting the generator from high currents, there must be generator powered welders on ships, oil rigs etc.

 

better drop gensetsteve a pm

Link to comment
Share on other sites

im currently running the 350 amp rated at 13.2kva on the 20kva gen and seems to be happy enough. i think these welders are designed to have a low power consumption to make them more versatile. planning to run the 500 on a 100kva.

 

is there a way of protecting the generator from high currents, there must be generator powered welders on ships, oil rigs etc.

 

better drop gensetsteve a pm

 

My knowledge on running welders is a bit thin as I tend to deal with big standbys for buildings. I know welders are very cruel on Gensets. I would talk to Genset in South Wales they are big into welders or mosa they should have some good info. If we have some big start up loads ie motors we install a permanent magnet generator or pm alternator. This set often has an avr and a separate transformer excitation. Means you can often install a much smaller set and once the load is running the generator is less likely to slobber on light load and glaze up the cylinders. Hope this helps if I think of anything else will post up.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  •  

  • Featured Adverts

About

Arbtalk.co.uk is a hub for the arboriculture industry in the UK.  
If you're just starting out and you need business, equipment, tech or training support you're in the right place.  If you've done it, made it, got a van load of oily t-shirts and have decided to give something back by sharing your knowledge or wisdom,  then you're welcome too.
If you would like to contribute to making this industry more effective and safe then welcome.
Just like a living tree, it'll always be a work in progress.
Please have a look around, sign up, share and contribute the best you have.

See you inside.

The Arbtalk Team

Follow us

Articles

×
×
  • Create New...

Important Information

We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.