what size generator do i need to power my kindlet 240 volts single phase


kindlett
 Share

Recommended Posts

We don't sell the Chinese stuff but you can pick them up on eBay for about £900 sometimes they last years if looked after often they last 15 minutes .

 

We sell a pramac p6000s last time I looked it was about £2500.00 +vat genuine yanmar engine and really quiet.

 

Hi Steve I'm told them P6000S are great thanks Jon

Link to comment
Share on other sites

Log in or register to remove this advert

  • Replies 22
  • Created
  • Last Reply

Top Posters In This Topic

If it's 3 times current why only double?

 

As Farmer Tom said its a rule of thumb. Not strictly true as depending on motor design starting current can be 10 times running current. It's just a useful average. When a motor starts it has virtually a short circuit through the windings, as it runs up the back emf opposes the incoming current which quickly drops to normal. This is why you probably have b rated breakers in your house but a motor needs slower acting c or even d rated breakers. A breaker size of 2 or 3 times running current normally does the job but do not over size as its job is to protect the cable not the motor as many think.

Bigger gensets have more power, heavier windings, bigger breakers and more inertia to help cope with the high motor starting current.

Link to comment
Share on other sites

Hi Steve I'm told them P6000S are great thanks Jon

 

Probably the best on the market. Not perfect as it's still only a single cyl air cooled engine but as good as you will get unless you spend over 6 k. Incredibly quiet but make sure you get the p6000s and not the p6000. I think I have sold one this week but need to check how much I pay for them now.

Link to comment
Share on other sites

As Farmer Tom said its a rule of thumb. Not strictly true as depending on motor design starting current can be 10 times running current. It's just a useful average. When a motor starts it has virtually a short circuit through the windings, as it runs up the back emf opposes the incoming current which quickly drops to normal. This is why you probably have b rated breakers in your house but a motor needs slower acting c or even d rated breakers. A breaker size of 2 or 3 times running current normally does the job but do not over size as its job is to protect the cable not the motor as many think.

 

Bigger gensets have more power, heavier windings, bigger breakers and more inertia to help cope with the high motor starting current.

 

 

Thanks to both of you. It just sounded a bit odd:-)

Link to comment
Share on other sites

A breaker size of 2 or 3 times running current normally does the job but do not over size as its job is to protect the cable not the motor as many think.

.

 

Thats if you are using household MCBs and veiw your motor as consumable!! If you value your motor use a proper motor circuit breaker that will protect both the motor and cable with thermal and magnetic trips.

Link to comment
Share on other sites

Thats if you are using household MCBs and veiw your motor as consumable!! If you value your motor use a proper motor circuit breaker that will protect both the motor and cable with thermal and magnetic trips.

 

The domestic house hold breakers are often more accurate and kinder to the windings than the stuff fitted to small generators as standard. Unless you spend a lot of money it will be difficult to get a breaker to prevent a gradual overload. If the breaker cuts out at exactly 10 amps then it will pop every time you start a motor. The best thing to protect your generator windings is the operator.

 

Guess how many amps you can build up gradually on a 13 amp plug fuse before it blows.

Link to comment
Share on other sites

The domestic house hold breakers are often more accurate and kinder to the windings than the stuff fitted to small generators as standard. Unless you spend a lot of money it will be difficult to get a breaker to prevent a gradual overload. If the breaker cuts out at exactly 10 amps then it will pop every time you start a motor. The best thing to protect your generator windings is the operator.

 

Guess how many amps you can build up gradually on a 13 amp plug fuse before it blows.

Your probably right about the std motor protection, but a properly sized motor circuit breaker will fully protect the motor against short circuit/locked rotor AND gradual thermal overload. Quick search on fleabay and theyre about £25-30 which aint alot to save your motor and associated downtime.

Link to comment
Share on other sites

Thats if you are using household MCBs and veiw your motor as consumable!! If you value your motor use a proper motor circuit breaker that will protect both the motor and cable with thermal and magnetic trips.

A household breaker trips in a quicker time than a motor rated breaker. The motor rated one is designed to trip slower to allow for the large starting current. Neither are designed to protect a motor. Both are thermally activated.

A motor should be protected by a motor overload which needs to be adjusted to maximum running current found on the motor plate. Again thermally activated.

 

For example a motor with a max running current of 5.9A could have a motor rated breaker C20 to protect the cable. C is trip time 20 is current carrying capacity. A heavily loaded motor with a heavy load such as a compressor might need a D rated trip to allow a longer start time drawing a high current.

The motor will be protected by a motor overload which on installation will be adjusted to 5.9A. This allows for the heavy start current but if the motor stalls the overload will trip to protect the motor.

Overloads are infinitely adjustable, breakers are available in set ratings.

Link to comment
Share on other sites

I think we're getting terminology mixed up. The motor circuit breaker I'm taliking about isnt a type D minature circuit breaker. Its a combined instantaneous and overload trip and is specifically intended to protect motors from short circuit and overload. Nothing like a household MCB as in minature circuit breaker. Typically a telemech GV2 or Siemens 3RV

Link to comment
Share on other sites

I think we're getting terminology mixed up. The motor circuit breaker I'm taliking about isnt a type D minature circuit breaker. Its a combined instantaneous and overload trip and is specifically intended to protect motors from short circuit and overload. Nothing like a household MCB as in minature circuit breaker. Typically a telemech GV2 or Siemens 3RV

 

In my day job we normally call the distribution board or cabinet mcbs "breakers" and any motor protection devices such as you have named "overloads".

Sorry for the mixup but it's common terminology with the engineers and electricians I deal with.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share


  •  

  • Featured Adverts

About

Arbtalk.co.uk is a hub for the arboriculture industry in the UK.  
If you're just starting out and you need business, equipment, tech or training support you're in the right place.  If you've done it, made it, got a van load of oily t-shirts and have decided to give something back by sharing your knowledge or wisdom,  then you're welcome too.
If you would like to contribute to making this industry more effective and safe then welcome.
Just like a living tree, it'll always be a work in progress.
Please have a look around, sign up, share and contribute the best you have.

See you inside.

The Arbtalk Team

Follow us

Articles

×
×
  • Create New...

Important Information

We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.