Jump to content

Log in or register to remove this advert

32A to 16A 3 phase question


Dilz
 Share

Recommended Posts

3 hours ago, GarethM said:

Yeap, it made life easier than explaining 3 phase to people.

 

We had a green light in the on/off switch mechanism too, so it was either green for go or red for no!.

Very good idea!! I take it you used to sell machinery or install it??

 

john..

Link to comment
Share on other sites

Log in or register to remove this advert

8 minutes ago, john87 said:

Very good idea!! I take it you used to sell machinery or install it??

I still sell & repair equipment and have moved almost entirely to single phase and transformer driven electronic BLDC type motors without any real loss in power.

 

Usual HSE type of thing, even now people seem to be gravitating even further to 110v.

  • Like 1
Link to comment
Share on other sites

WWW.THOMANN.DE

CEE Adapter 32A - 16A Mobile plastic distributor, type St. Anton-2f IP44 with bracket, 1x CEE connector 32 A 5p 400V...

 

Using one of these seems a legit way to go about it.   

 

Would it make sense to pull this in to the 32A outlet and then run a 16A cable to the machine or would a 32a cable be best to run from the outlet? Going to need about 30 - 35m of cable I reckon. 

 

 

 

Link to comment
Share on other sites

48 minutes ago, Dilz said:
WWW.THOMANN.DE

CEE Adapter 32A - 16A Mobile plastic distributor, type St. Anton-2f IP44 with bracket, 1x CEE connector 32 A 5p 400V...

 

Using one of these seems a legit way to go about it.   

 

Would it make sense to pull this in to the 32A outlet and then run a 16A cable to the machine or would a 32a cable be best to run from the outlet? Going to need about 30 - 35m of cable I reckon. 

 

 

 

 

As i think Gareth is about to mention, the extension lead is not going to be that simple and you really need to get an electrician with a brain involved. That is a very long run.. It is NOT NOT NOT, just a question of getting a "16A" extension lead..

 

You see, at that length of run, EFLI and volt drop are going to be the governing factors for the following reasons..

1, If the volt drop is too high, the motors will struggle to start if they start at all.

2, If EFLI is too high, in the event of a fault, the breakers will either trip too slowly or not at all. Either way, it will result in damage or electrocution..

 

I once sold a compressor to a farmer They connected it to a very long run of 2.5 twin and earth, The thing barely started...

A few days later, said farmer turns up all irate.. I go and have a look, and what had happened, is the motor had failed to start. As it was such a long run of cable, even though there was effectively a dead short, the "circuit" could not pull enough current to trip the breaker, so the power stayed on and the whole lot got hotter adn hotter until the motor had literally melted into a blob of aluminium and copper..

 

You see, a circuit breaker is selected to suit the load.. THEN a cable is selected on the basis of Volt drop and EFLI, which means that you could need a cable suited to, say, 70A for your 16A load..

 

Tell us exactly what it is you want to run and we can advise further..

 

john..

  • Like 1
Link to comment
Share on other sites

26 minutes ago, GarethM said:

Fair enough, how much power do you need ?.

Hi Gareth,

 

Ok, an 8kw motor, so that is 8000/1.732/400 = 11.5A but then guessing PF .8 and efficiency 90%  just over 16A ??

Then you would need an allowance for starting currents..

 

Pretty big cable??

 

john..

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share


  •  

  • Featured Adverts

About

Arbtalk.co.uk is a hub for the arboriculture industry in the UK.  
If you're just starting out and you need business, equipment, tech or training support you're in the right place.  If you've done it, made it, got a van load of oily t-shirts and have decided to give something back by sharing your knowledge or wisdom,  then you're welcome too.
If you would like to contribute to making this industry more effective and safe then welcome.
Just like a living tree, it'll always be a work in progress.
Please have a look around, sign up, share and contribute the best you have.

See you inside.

The Arbtalk Team

Follow us

Articles

×
×
  • Create New...

Important Information

We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.